If my numbers are correct, 1/2" soft copper pipe (type M) has a cross-sectional wall size that's just over that of 2 AWG wire (33.8 sq mm vs 33.6 sq mm), so flattened copper pipe would make a good bus bar, with at least a current capacity of 190 amps (at 105 degrees C). I could use 3/4" copper pipe instead, but that doesn't seem necessary &
I haven't run the numbers on anything larger yet.
3/4" type M copper pipe appears to have a cross-sectional area that's just over the size of 1/0 copper wire, and can probably handle equivalent current to that.
1" type M copper appears to have a cross-sectional area that's just over halfway between 2/0 and 3/0 copper cable...
My homework/showing my work, just to allow others to check my figures:
{Nominal outside diameter of the pipe/2 squared x Pi (radius squared x Pi)} - {nominal inside diameter of the pipe/2 squared x Pi} should equal just the area of the wall thickness.
Conversion of square inches to square mm is done by multiplying the sq inches x 25.4 x 25.4 (squared).
Most of the charts showing pipe sizes are listing in SAE/English units, ie. inches, not metric, but the chart I found showing wire gage equivalents was a chart showing everything in metric (mm). Wire sizes larger than 4/0 use the metric system anyway. The European norm is to use a comma delimited where Americans are accustomed to using a period, so be mindful of that when reading that chart.
https://www.sab-cable.com/cables-wires-harnessing-temperature-measurement/technical-data/cables-and-wires/american-cable-stranding.html
Types K and L are thicker walled pipe, so they could support even higher current than these examples.
https://pexuniverse.com/copper-pipe-dimensions-specs
After finding the next smaller size wire on the chart, one can then cross-reference the ampacity charts for that size wire, using whichever temperature column one is willing to insulate to. This post is dedicated to my high school math teacher Ms. Klingsic, who insisted that EVERYONE wants to see my work... đ